Author Question: Use Figures 89-27 and Table 89-2 to determine the correct amount of additional charge for a new ... (Read 18 times)

naturalchemist

  • Hero Member
  • *****
  • Posts: 542
Use Figures 89-27 and Table 89-2 to determine the correct amount of additional charge for a new split system with a 40 foot line set and a 3/8 liquid line. The factory charge includes enough refrigerant for 15 feet of line.
 
  What will be an ideal response?

Question 2

Use the information on the data plate in Figure 89-24 to determine the maximum circuit breaker size for the unit.
 
  What will be an ideal response?



Related Topics

Need homework help now?

Ask unlimited questions for free

Ask a Question
Marked as best answer by a Subject Expert

blakeserpa

  • Sr. Member
  • ****
  • Posts: 338
Answer to Question 1

40 feet - 15 feet = 25 feet additional line
25  0.6 ounces

Answer to Question 2

The circuit breaker should be no larger than the maximum size on the dataplate 50 amps.




naturalchemist

  • Member
  • Posts: 542
Reply 2 on: Jul 26, 2018
Thanks for the timely response, appreciate it


Liddy

  • Member
  • Posts: 342
Reply 3 on: Yesterday
Excellent

 

Did you know?

Lower drug doses for elderly patients should be used first, with titrations of the dose as tolerated to prevent unwanted drug-related pharmacodynamic effects.

Did you know?

There are more sensory neurons in the tongue than in any other part of the body.

Did you know?

Atropine, along with scopolamine and hyoscyamine, is found in the Datura stramonium plant, which gives hallucinogenic effects and is also known as locoweed.

Did you know?

Congestive heart failure is a serious disorder that carries a reduced life expectancy. Heart failure is usually a chronic illness, and it may worsen with infection or other physical stressors.

Did you know?

The first oral chemotherapy drug for colon cancer was approved by FDA in 2001.

For a complete list of videos, visit our video library