Author Question: What is the difference between vent sizing for natural draft appliances and fan assisted appliances? ... (Read 42 times)

RODY.ELKHALIL

  • Hero Member
  • *****
  • Posts: 591
What is the difference between vent sizing for natural draft appliances and fan assisted appliances?
 
  What will be an ideal response?

Question 2

What size should the combustion air openings be for a room with an 80,000 BTU/hr input furnace and a 35,000 BTU/hr water heater if the openings are opening directly into a ventilated attic and a ventilated crawlspace?
 
  What will be an ideal response?



morganmarie791

  • Sr. Member
  • ****
  • Posts: 336
Answer to Question 1

Natural draft vents only have the maximum capacity listed in the tables. Fan assisted columns list both a minimum and a maximum appliance capacity for each vent size.

Answer to Question 2

80,000 + 35,000 = 115,000 total input 115,000 / 4,000 = 28.75 square inches each



Related Topics

Need homework help now?

Ask unlimited questions for free

Ask a Question
 

Did you know?

Certain chemicals, after ingestion, can be converted by the body into cyanide. Most of these chemicals have been removed from the market, but some old nail polish remover, solvents, and plastics manufacturing solutions can contain these substances.

Did you know?

In 1886, William Bates reported on the discovery of a substance produced by the adrenal gland that turned out to be epinephrine (adrenaline). In 1904, this drug was first artificially synthesized by Friedrich Stolz.

Did you know?

There are 60,000 miles of blood vessels in every adult human.

Did you know?

Alzheimer's disease affects only about 10% of people older than 65 years of age. Most forms of decreased mental function and dementia are caused by disuse (letting the mind get lazy).

Did you know?

After a vasectomy, it takes about 12 ejaculations to clear out sperm that were already beyond the blocked area.

For a complete list of videos, visit our video library