Author Question: Why do some systems have discharge check valves? What will be an ideal ... (Read 47 times)

bclement10

  • Hero Member
  • *****
  • Posts: 560
Why do some systems have discharge check valves?
 
  What will be an ideal response?

Question 2

Explain the following data plate ratings:
 
  What will be an ideal response?



SomethingSomething

  • Sr. Member
  • ****
  • Posts: 323
Answer to Question 1

To prevent liquid refrigerant from flowing back to the compressor from the condenser during the off cycle of the system.

Answer to Question 2

RLA - rating load amps of the compressor, gives the approximate operating compressor amp draw
FLA - full load amps, gives the approximate operating fan amp draw Minimum Voltage -lowest voltage unit can safely operate Maximum Voltage - highest voltage unit can safely operate

Minimum Circuit Ampacity - power wire to unit must be able to carry at least this many amps, used to size the power wire.
Maximum Overcurrent Protection - largest fuse or breaker that may be used



Related Topics

Need homework help now?

Ask unlimited questions for free

Ask a Question
 

Did you know?

Elderly adults are living longer, and causes of death are shifting. At the same time, autopsy rates are at or near their lowest in history.

Did you know?

After 5 years of being diagnosed with rheumatoid arthritis, one every three patients will no longer be able to work.

Did you know?

The effects of organophosphate poisoning are referred to by using the abbreviations “SLUD” or “SLUDGE,” It stands for: salivation, lacrimation, urination, defecation, GI upset, and emesis.

Did you know?

Thyroid conditions cause a higher risk of fibromyalgia and chronic fatigue syndrome.

Did you know?

Anti-aging claims should not ever be believed. There is no supplement, medication, or any other substance that has been proven to slow or stop the aging process.

For a complete list of videos, visit our video library