Author Question: Describe the procedure for purging a two pipe system? What will be an ideal ... (Read 22 times)

c0205847

  • Hero Member
  • *****
  • Posts: 531
Describe the procedure for purging a two pipe system?
 
  What will be an ideal response?

Question 2

What is the firing rate of a furnace with a Beckett AFG-FG burner and a 0.75 gph 70-B nozzle? (refer to Table 55-1)
 
  What will be an ideal response?



joanwhite

  • Sr. Member
  • ****
  • Posts: 308
Answer to Question 1

The two pipe system is self purging, but typically it takes more than one safety timing period to clear all the air. Pushing the reset a couple of times may be necessary.

Answer to Question 2

105,000 BTU per hour