An electric heater is rated at 300 W when used in a 110-V circuit. The safety fuse in the circuit can accommodate 15 A of current. How many heaters can be safely operated in the circuit?
 
  A) 2
  B) 3
  C) 4
  D) 5
  E) more than 5

Question 2

A certain bulb with a resistance of 95 ohms and labeled 150 W is designated for use in a
 
  A) 120-V circuit.
  B) 240-V circuit.
  C) either
  D) not enough information



moormoney

  • Sr. Member
  • ****
  • Posts: 326
Answer to Question 1

Answer: D

Answer to Question 2

Answer: A



Related Topics

Need homework help now?

Ask unlimited questions for free

Ask a Question
 

Did you know?

It is important to read food labels and choose foods with low cholesterol and saturated trans fat. You should limit saturated fat to no higher than 6% of daily calories.

Did you know?

The strongest synthetic topical retinoid drug available, tazarotene, is used to treat sun-damaged skin, acne, and psoriasis.

Did you know?

Eating carrots will improve your eyesight. Carrots are high in vitamin A (retinol), which is essential for good vision. It can also be found in milk, cheese, egg yolks, and liver.

Did you know?

Only 12 hours after an egg cell is fertilized by a sperm cell, the egg cell starts to divide. As it continues to divide, it moves along the fallopian tube toward the uterus at about 1 inch per day.

Did you know?

On average, someone in the United States has a stroke about every 40 seconds. This is about 795,000 people per year.

For a complete list of videos, visit our video library