The microprocessor control board in a packaged heat pump has the correct inputs and outputs to energize
  the reversing valve, but the valve does not energize. What is the next logical step in the troubleshooting
  process?
 
  a. Replace the control board
  b. Check the control board further for defects
  c. Check the reversing valve coil
  d. Replace the reversing valve

Question 2

With a dual-fuel heat pump, at what outdoor temperature is the heat pump typically locked out and the
  furnace activated to provide heat?
 
  a. Below 25F
  b. Below freezing
  c. Slightly above the structure's balance point
  d. 10F below the balance point



Related Topics

Need homework help now?

Ask unlimited questions for free

Ask a Question
Marked as best answer by a Subject Expert

SamMuagrove

  • Sr. Member
  • ****
  • Posts: 312
Answer to Question 1

c

Answer to Question 2

c





 

Did you know?

The heart is located in the center of the chest, with part of it tipped slightly so that it taps against the left side of the chest.

Did you know?

In 2012, nearly 24 milliion Americans, aged 12 and older, had abused an illicit drug, according to the National Institute on Drug Abuse (NIDA).

Did you know?

In ancient Rome, many of the richer people in the population had lead-induced gout. The reason for this is unclear. Lead poisoning has also been linked to madness.

Did you know?

Alzheimer's disease affects only about 10% of people older than 65 years of age. Most forms of decreased mental function and dementia are caused by disuse (letting the mind get lazy).

Did you know?

The strongest synthetic topical retinoid drug available, tazarotene, is used to treat sun-damaged skin, acne, and psoriasis.

For a complete list of videos, visit our video library