Author Question: What friction rate should be used to size a duct for a design friction rate of 0.12 in WC if the ... (Read 47 times)

BRWH

  • Hero Member
  • *****
  • Posts: 553
What friction rate should be used to size a duct for a design friction rate of 0.12 in WC if the duct has a total equivalent length of 150 ft?
 
  A) 0.12  (150/100 ) = 0.12  1.5 = 0.18 in WC B) 0.12  (100/150 ) = 0.67  0.12 = 0.08 in WC
  C) 0.1 in wc because that is the standard factor D) 0.12 in WC because the duct length is irrelevant

Question 2

Organizations that provide duct installation standards and guidelines include:
 
  A) EPA and OSHA.
  B) ACCA and SMACNA.
  C) Underwriters Laboratories and the National Fire Protection Association.
  D) AHRI and HVAC Excellence.



chloejackso

  • Sr. Member
  • ****
  • Posts: 316
Answer to Question 1

B

Answer to Question 2

B



Related Topics

Need homework help now?

Ask unlimited questions for free

Ask a Question


 

Did you know?

Signs of depression include feeling sad most of the time for 2 weeks or longer; loss of interest in things normally enjoyed; lack of energy; sleep and appetite disturbances; weight changes; feelings of hopelessness, helplessness, or worthlessness; an inability to make decisions; and thoughts of death and suicide.

Did you know?

Approximately one in three babies in the United States is now delivered by cesarean section. The number of cesarean sections in the United States has risen 46% since 1996.

Did you know?

Sildenafil (Viagra®) has two actions that may be of consequence in patients with heart disease. It can lower the blood pressure, and it can interact with nitrates. It should never be used in patients who are taking nitrates.

Did you know?

Multiple experimental evidences have confirmed that at the molecular level, cancer is caused by lesions in cellular DNA.

Did you know?

The horizontal fraction bar was introduced by the Arabs.

For a complete list of videos, visit our video library