The refrigerant R-22 in a system component has a pressure of 70 psig and a temperature of 50F. Is it saturated, superheated, or subcooled?
 
  What will be an ideal response?

Question 2

If the input in BTUs per hour if the heating capacity of the gas is 950 BTUs per cubic foot?
 
  What will be an ideal response?



Related Topics

Need homework help now?

Ask unlimited questions for free

Ask a Question
Marked as best answer by a Subject Expert

ryhom

  • Sr. Member
  • ****
  • Posts: 366
Answer to Question 1

R-22 at 70 psig is saturated at just over 40F. Since 50F is greater than 40F, this refrigerant is superheated.

Answer to Question 2

60 cubic feet x 950 BTU/cubic foot = 57,000 BTUs per hour




wenmo

  • Member
  • Posts: 540
Reply 2 on: Jul 26, 2018
Excellent


Dinolord

  • Member
  • Posts: 313
Reply 3 on: Yesterday
Wow, this really help

 

Did you know?

Serum cholesterol testing in adults is recommended every 1 to 5 years. People with diabetes and a family history of high cholesterol should be tested even more frequently.

Did you know?

By definition, when a medication is administered intravenously, its bioavailability is 100%.

Did you know?

After a vasectomy, it takes about 12 ejaculations to clear out sperm that were already beyond the blocked area.

Did you know?

The longest a person has survived after a heart transplant is 24 years.

Did you know?

Everyone has one nostril that is larger than the other.

For a complete list of videos, visit our video library