The refrigerant R-22 in a system component has a pressure of 70 psig and a temperature of 50F. Is it saturated, superheated, or subcooled?
 
  What will be an ideal response?

Question 2

If the input in BTUs per hour if the heating capacity of the gas is 950 BTUs per cubic foot?
 
  What will be an ideal response?



Related Topics

Need homework help now?

Ask unlimited questions for free

Ask a Question
Marked as best answer by a Subject Expert

ryhom

  • Sr. Member
  • ****
  • Posts: 366
Answer to Question 1

R-22 at 70 psig is saturated at just over 40F. Since 50F is greater than 40F, this refrigerant is superheated.

Answer to Question 2

60 cubic feet x 950 BTU/cubic foot = 57,000 BTUs per hour




wenmo

  • Member
  • Posts: 540
Reply 2 on: Jul 26, 2018
Gracias!


lkanara2

  • Member
  • Posts: 329
Reply 3 on: Yesterday
Wow, this really help

 

Did you know?

Nearly 31 million adults in America have a total cholesterol level that is more than 240 mg per dL.

Did you know?

Eating carrots will improve your eyesight. Carrots are high in vitamin A (retinol), which is essential for good vision. It can also be found in milk, cheese, egg yolks, and liver.

Did you know?

Alzheimer's disease affects only about 10% of people older than 65 years of age. Most forms of decreased mental function and dementia are caused by disuse (letting the mind get lazy).

Did you know?

On average, the stomach produces 2 L of hydrochloric acid per day.

Did you know?

The FDA recognizes 118 routes of administration.

For a complete list of videos, visit our video library