Author Question: According to Table 26-31 what would be the recommended support spacing for 2 1/8 inch type L copper ... (Read 36 times)

Lobcity

  • Hero Member
  • *****
  • Posts: 524
According to Table 26-31 what would be the recommended support spacing for 2 1/8 inch type L copper pipe?
 
  What will be an ideal response?

Question 2

If the condenser pressure of the above system is 317 psig, how much subcooling will be required to offset the pressure drop created by the vertical lift?
 
  What will be an ideal response?



xiaomengxian

  • Sr. Member
  • ****
  • Posts: 311
Answer to Question 1

The maximum distance between supports for 2 1/8 type L copper is 10 feet.

Answer to Question 2

317  13 = 304 psig. Total subcooling is calculated by determining the saturation temperature of 317 psig R410a that is approximately 100
and the saturation temperature of R410a at 304 psig, which is approximately 97F. 4F of subcooling will be required to prevent flash gas. 100F  97 = 3F + 1F = 4F



Related Topics

Need homework help now?

Ask unlimited questions for free

Ask a Question
 

Did you know?

There are 60,000 miles of blood vessels in every adult human.

Did you know?

There are approximately 3 million unintended pregnancies in the United States each year.

Did you know?

Certain rare plants containing cyanide include apricot pits and a type of potato called cassava. Fortunately, only chronic or massive ingestion of any of these plants can lead to serious poisoning.

Did you know?

Before a vaccine is licensed in the USA, the Food and Drug Administration (FDA) reviews it for safety and effectiveness. The CDC then reviews all studies again, as well as the American Academy of Pediatrics and the American Academy of Family Physicians. Every lot of vaccine is tested before administration to the public, and the FDA regularly inspects vaccine manufacturers' facilities.

Did you know?

Thyroid conditions may make getting pregnant impossible.

For a complete list of videos, visit our video library