According to Table 26-31 what would be the recommended support spacing for 2 1/8 inch type L copper pipe?
 
  What will be an ideal response?

Question 2

If the condenser pressure of the above system is 317 psig, how much subcooling will be required to offset the pressure drop created by the vertical lift?
 
  What will be an ideal response?



xiaomengxian

  • Sr. Member
  • ****
  • Posts: 311
Answer to Question 1

The maximum distance between supports for 2 1/8 type L copper is 10 feet.

Answer to Question 2

317  13 = 304 psig. Total subcooling is calculated by determining the saturation temperature of 317 psig R410a that is approximately 100
and the saturation temperature of R410a at 304 psig, which is approximately 97F. 4F of subcooling will be required to prevent flash gas. 100F  97 = 3F + 1F = 4F



Related Topics

Need homework help now?

Ask unlimited questions for free

Ask a Question
 

Did you know?

About 80% of major fungal systemic infections are due to Candida albicans. Another form, Candida peritonitis, occurs most often in postoperative patients. A rare disease, Candida meningitis, may follow leukemia, kidney transplant, other immunosuppressed factors, or when suffering from Candida septicemia.

Did you know?

There are 60,000 miles of blood vessels in every adult human.

Did you know?

Blood in the urine can be a sign of a kidney stone, glomerulonephritis, or other kidney problems.

Did you know?

Vaccines prevent between 2.5 and 4 million deaths every year.

Did you know?

Vaccines cause herd immunity. If the majority of people in a community have been vaccinated against a disease, an unvaccinated person is less likely to get the disease since others are less likely to become sick from it and spread the disease.

For a complete list of videos, visit our video library