Author Question: What should a service technician do if they find a blown fuse in series with the low voltage side of ... (Read 127 times)

evelyn o bentley

  • Hero Member
  • *****
  • Posts: 564
What should a service technician do if they find a blown fuse in series with the low voltage side of the transformer?
 
  What will be an ideal response?

Question 2

What should a service technician do if they find a blown fuse in the unit disconnect switch during the preliminary inspection?
 
  What will be an ideal response?



Related Topics

Need homework help now?

Ask unlimited questions for free

Ask a Question
Marked as best answer by a Subject Expert

dajones82

  • Sr. Member
  • ****
  • Posts: 359
Answer to Question 1

Check all low voltage controls for shorts and grounds. After replacing the fuse, check the voltage output of the secondary side of the transformer. Then monitor that voltage while running the system through its different operating cycles.

Answer to Question 2

Check all major loads for shorts and grounds. After replacing the fuse, check the system amp draw and compare it to the data plate rating. Finally, check the amp draw of each major load individually.




evelyn o bentley

  • Member
  • Posts: 564
Reply 2 on: Jul 26, 2018
Great answer, keep it coming :)


vickyvicksss

  • Member
  • Posts: 351
Reply 3 on: Yesterday
Wow, this really help

 

Did you know?

Bacteria have flourished on the earth for over three billion years. They were the first life forms on the planet.

Did you know?

Opium has influenced much of the world's most popular literature. The following authors were all opium users, of varying degrees: Lewis Carroll, Charles, Dickens, Arthur Conan Doyle, and Oscar Wilde.

Did you know?

Sperm cells are so tiny that 400 to 500 million (400,000,000–500,000,000) of them fit onto 1 tsp.

Did you know?

Vital signs (blood pressure, temperature, pulse rate, respiration rate) should be taken before any drug administration. Patients should be informed not to use tobacco or caffeine at least 30 minutes before their appointment.

Did you know?

Certain chemicals, after ingestion, can be converted by the body into cyanide. Most of these chemicals have been removed from the market, but some old nail polish remover, solvents, and plastics manufacturing solutions can contain these substances.

For a complete list of videos, visit our video library