A pressure-time-temperature defrost system goes into defrost with very little frost on the bottom of the coil. Describe the major cause of and solution to this problem.
 
  What will be an ideal response?

Question 2

Where are the specific enthalpy lines and how are they marked?
 
  What will be an ideal response?



vickybb89

  • Sr. Member
  • ****
  • Posts: 347
Answer to Question 1

The major cause of this action is a dirty outdoor coil, which causes an increased air pressure drop across the outdoor coil. Cleaning the coil solves this problem.

Answer to Question 2

The specific enthalpy lines are vertical lines going from top to bottom; the scale is shown along the top and bottom of the PH diagram. The units are given in Btu per pound of refrigerant, Btu/lb.



Related Topics

Need homework help now?

Ask unlimited questions for free

Ask a Question
 

Did you know?

Urine turns bright yellow if larger than normal amounts of certain substances are consumed; one of these substances is asparagus.

Did you know?

There are more sensory neurons in the tongue than in any other part of the body.

Did you know?

Approximately 70% of expectant mothers report experiencing some symptoms of morning sickness during the first trimester of pregnancy.

Did you know?

For pediatric patients, intravenous fluids are the most commonly cited products involved in medication errors that are reported to the USP.

Did you know?

According to the FDA, adverse drug events harmed or killed approximately 1,200,000 people in the United States in the year 2015.

For a complete list of videos, visit our video library