Author Question: A pressure-time-temperature defrost system goes into defrost with very little frost on the bottom of ... (Read 195 times)

RRMR

  • Hero Member
  • *****
  • Posts: 557
A pressure-time-temperature defrost system goes into defrost with very little frost on the bottom of the coil. Describe the major cause of and solution to this problem.
 
  What will be an ideal response?

Question 2

Where are the specific enthalpy lines and how are they marked?
 
  What will be an ideal response?



vickybb89

  • Sr. Member
  • ****
  • Posts: 347
Answer to Question 1

The major cause of this action is a dirty outdoor coil, which causes an increased air pressure drop across the outdoor coil. Cleaning the coil solves this problem.

Answer to Question 2

The specific enthalpy lines are vertical lines going from top to bottom; the scale is shown along the top and bottom of the PH diagram. The units are given in Btu per pound of refrigerant, Btu/lb.



Related Topics

Need homework help now?

Ask unlimited questions for free

Ask a Question
 

Did you know?

More than nineteen million Americans carry the factor V gene that causes blood clots, pulmonary embolism, and heart disease.

Did you know?

Alcohol acts as a diuretic. Eight ounces of water is needed to metabolize just 1 ounce of alcohol.

Did you know?

Many supplement containers do not even contain what their labels say. There are many documented reports of products containing much less, or more, that what is listed on their labels. They may also contain undisclosed prescription drugs and even contaminants.

Did you know?

Congestive heart failure is a serious disorder that carries a reduced life expectancy. Heart failure is usually a chronic illness, and it may worsen with infection or other physical stressors.

Did you know?

The Romans did not use numerals to indicate fractions but instead used words to indicate parts of a whole.

For a complete list of videos, visit our video library