A pressure-time-temperature defrost system goes into defrost with very little frost on the bottom of the coil. Describe the major cause of and solution to this problem.
 
  What will be an ideal response?

Question 2

Where are the specific enthalpy lines and how are they marked?
 
  What will be an ideal response?



vickybb89

  • Sr. Member
  • ****
  • Posts: 347
Answer to Question 1

The major cause of this action is a dirty outdoor coil, which causes an increased air pressure drop across the outdoor coil. Cleaning the coil solves this problem.

Answer to Question 2

The specific enthalpy lines are vertical lines going from top to bottom; the scale is shown along the top and bottom of the PH diagram. The units are given in Btu per pound of refrigerant, Btu/lb.



Related Topics

Need homework help now?

Ask unlimited questions for free

Ask a Question
 

Did you know?

The Babylonians wrote numbers in a system that used 60 as the base value rather than the number 10. They did not have a symbol for "zero."

Did you know?

Blood is approximately twice as thick as water because of the cells and other components found in it.

Did you know?

No drugs are available to relieve parathyroid disease. Parathyroid disease is caused by a parathyroid tumor, and it needs to be removed by surgery.

Did you know?

The B-complex vitamins and vitamin C are not stored in the body and must be replaced each day.

Did you know?

In 1885, the Lloyd Manufacturing Company of Albany, New York, promoted and sold "Cocaine Toothache Drops" at 15 cents per bottle! In 1914, the Harrison Narcotic Act brought the sale and distribution of this drug under federal control.

For a complete list of videos, visit our video library