A pressure-time-temperature defrost system goes into defrost with very little frost on the bottom of the coil. Describe the major cause of and solution to this problem.
 
  What will be an ideal response?

Question 2

Where are the specific enthalpy lines and how are they marked?
 
  What will be an ideal response?



vickybb89

  • Sr. Member
  • ****
  • Posts: 347
Answer to Question 1

The major cause of this action is a dirty outdoor coil, which causes an increased air pressure drop across the outdoor coil. Cleaning the coil solves this problem.

Answer to Question 2

The specific enthalpy lines are vertical lines going from top to bottom; the scale is shown along the top and bottom of the PH diagram. The units are given in Btu per pound of refrigerant, Btu/lb.



Related Topics

Need homework help now?

Ask unlimited questions for free

Ask a Question
 

Did you know?

Addicts to opiates often avoid treatment because they are afraid of withdrawal. Though unpleasant, with proper management, withdrawal is rarely fatal and passes relatively quickly.

Did you know?

About 60% of newborn infants in the United States are jaundiced; that is, they look yellow. Kernicterus is a form of brain damage caused by excessive jaundice. When babies begin to be affected by excessive jaundice and begin to have brain damage, they become excessively lethargic.

Did you know?

Approximately 25% of all reported medication errors result from some kind of name confusion.

Did you know?

Your chance of developing a kidney stone is 1 in 10. In recent years, approximately 3.7 million people in the United States were diagnosed with a kidney disease.

Did you know?

Between 1999 and 2012, American adults with high total cholesterol decreased from 18.3% to 12.9%

For a complete list of videos, visit our video library