Author Question: The refrigerant R-22 in a system component has a pressure of 70 psig and a temperature of 50F. Is it ... (Read 90 times)

wenmo

  • Hero Member
  • *****
  • Posts: 540
The refrigerant R-22 in a system component has a pressure of 70 psig and a temperature of 50F. Is it saturated, superheated, or subcooled?
 
  What will be an ideal response?

Question 2

If the input in BTUs per hour if the heating capacity of the gas is 950 BTUs per cubic foot?
 
  What will be an ideal response?



Related Topics

Need homework help now?

Ask unlimited questions for free

Ask a Question
Marked as best answer by a Subject Expert

ryhom

  • Sr. Member
  • ****
  • Posts: 366
Answer to Question 1

R-22 at 70 psig is saturated at just over 40F. Since 50F is greater than 40F, this refrigerant is superheated.

Answer to Question 2

60 cubic feet x 950 BTU/cubic foot = 57,000 BTUs per hour




wenmo

  • Member
  • Posts: 540
Reply 2 on: Jul 26, 2018
:D TYSM


jomama

  • Member
  • Posts: 346
Reply 3 on: Yesterday
YES! Correct, THANKS for helping me on my review

 

Did you know?

It is widely believed that giving a daily oral dose of aspirin to heart attack patients improves their chances of survival because the aspirin blocks the formation of new blood clots.

Did you know?

More than 30% of American adults, and about 12% of children utilize health care approaches that were developed outside of conventional medicine.

Did you know?

If you could remove all of your skin, it would weigh up to 5 pounds.

Did you know?

Eat fiber! A diet high in fiber can help lower cholesterol levels by as much as 10%.

Did you know?

There are immediate benefits of chiropractic adjustments that are visible via magnetic resonance imaging (MRI). It shows that spinal manipulation therapy is effective in decreasing pain and increasing the gaps between the vertebrae, reducing pressure that leads to pain.

For a complete list of videos, visit our video library