Author Question: A pressure-time-temperature defrost system goes into defrost with very little frost on the bottom of ... (Read 150 times)

RRMR

  • Hero Member
  • *****
  • Posts: 557
A pressure-time-temperature defrost system goes into defrost with very little frost on the bottom of the coil. Describe the major cause of and solution to this problem.
 
  What will be an ideal response?

Question 2

Where are the specific enthalpy lines and how are they marked?
 
  What will be an ideal response?



vickybb89

  • Sr. Member
  • ****
  • Posts: 347
Answer to Question 1

The major cause of this action is a dirty outdoor coil, which causes an increased air pressure drop across the outdoor coil. Cleaning the coil solves this problem.

Answer to Question 2

The specific enthalpy lines are vertical lines going from top to bottom; the scale is shown along the top and bottom of the PH diagram. The units are given in Btu per pound of refrigerant, Btu/lb.



Related Topics

Need homework help now?

Ask unlimited questions for free

Ask a Question
 

Did you know?

Medication errors are three times higher among children and infants than with adults.

Did you know?

Approximately one in three babies in the United States is now delivered by cesarean section. The number of cesarean sections in the United States has risen 46% since 1996.

Did you know?

Asthma is the most common chronic childhood disease in the world. Most children who develop asthma have symptoms before they are 5 years old.

Did you know?

It is important to read food labels and choose foods with low cholesterol and saturated trans fat. You should limit saturated fat to no higher than 6% of daily calories.

Did you know?

Every 10 seconds, a person in the United States goes to the emergency room complaining of head pain. About 1.2 million visits are for acute migraine attacks.

For a complete list of videos, visit our video library