Author Question: Which of the following will cause the number of conductors allowed in a box to be reduced? A) The ... (Read 124 times)

karlynnae

  • Hero Member
  • *****
  • Posts: 599
Which of the following will cause the number of conductors allowed in a box to be reduced?
 
  A) The shape of the box
  B) The use of cable clamps
  C) Locating the box in a wet area
  D) The addition of box extension rings

Question 2

Which of the following counts as two conductors when used in a box?
 
  A) Each fixture stud
  B) Each looped conductor over 6
  C) Each looped conductor over 12
  D) Each cable clamp



Related Topics

Need homework help now?

Ask unlimited questions for free

Ask a Question
Marked as best answer by a Subject Expert

scrocafella

  • Sr. Member
  • ****
  • Posts: 346
Answer to Question 1

Answer: B

Answer to Question 2

Answer: C




karlynnae

  • Member
  • Posts: 599
Reply 2 on: Jul 24, 2018
Great answer, keep it coming :)


daiying98

  • Member
  • Posts: 354
Reply 3 on: Yesterday
:D TYSM

 

Did you know?

The first successful kidney transplant was performed in 1954 and occurred in Boston. A kidney from an identical twin was transplanted into his dying brother's body and was not rejected because it did not appear foreign to his body.

Did you know?

Many supplement containers do not even contain what their labels say. There are many documented reports of products containing much less, or more, that what is listed on their labels. They may also contain undisclosed prescription drugs and even contaminants.

Did you know?

Russia has the highest death rate from cardiovascular disease followed by the Ukraine, Romania, Hungary, and Poland.

Did you know?

Thyroid conditions may make getting pregnant impossible.

Did you know?

The longest a person has survived after a heart transplant is 24 years.

For a complete list of videos, visit our video library