Author Question: Use Figures 89-27 and Table 89-2 to determine the correct amount of additional charge for a new ... (Read 53 times)

naturalchemist

  • Hero Member
  • *****
  • Posts: 542
Use Figures 89-27 and Table 89-2 to determine the correct amount of additional charge for a new split system with a 40 foot line set and a 3/8 liquid line. The factory charge includes enough refrigerant for 15 feet of line.
 
  What will be an ideal response?

Question 2

Use the information on the data plate in Figure 89-24 to determine the maximum circuit breaker size for the unit.
 
  What will be an ideal response?



Related Topics

Need homework help now?

Ask unlimited questions for free

Ask a Question
Marked as best answer by a Subject Expert

blakeserpa

  • Sr. Member
  • ****
  • Posts: 338
Answer to Question 1

40 feet - 15 feet = 25 feet additional line
25  0.6 ounces

Answer to Question 2

The circuit breaker should be no larger than the maximum size on the dataplate 50 amps.




naturalchemist

  • Member
  • Posts: 542
Reply 2 on: Jul 26, 2018
Great answer, keep it coming :)


vickybb89

  • Member
  • Posts: 347
Reply 3 on: Yesterday
Gracias!

 

Did you know?

Many people have small pouches in their colons that bulge outward through weak spots. Each pouch is called a diverticulum. About 10% of Americans older than age 40 years have diverticulosis, which, when the pouches become infected or inflamed, is called diverticulitis. The main cause of diverticular disease is a low-fiber diet.

Did you know?

Urine turns bright yellow if larger than normal amounts of certain substances are consumed; one of these substances is asparagus.

Did you know?

There are 20 feet of blood vessels in each square inch of human skin.

Did you know?

About 3.2 billion people, nearly half the world population, are at risk for malaria. In 2015, there are about 214 million malaria cases and an estimated 438,000 malaria deaths.

Did you know?

Automated pill dispensing systems have alarms to alert patients when the correct dosing time has arrived. Most systems work with many varieties of medications, so patients who are taking a variety of drugs can still be in control of their dose regimen.

For a complete list of videos, visit our video library