Author Question: How do the Test and Balance procedures for a zoned system differ from a non-zoned system. What ... (Read 113 times)

EY67

  • Hero Member
  • *****
  • Posts: 531
How do the Test and Balance procedures for a zoned system differ from a non-zoned system.
 
  What will be an ideal response?

Question 2

Why must the copper fitting be cleaned before brazing it?
 
  What will be an ideal response?



Related Topics

Need homework help now?

Ask unlimited questions for free

Ask a Question
Marked as best answer by a Subject Expert

chloejackso

  • Sr. Member
  • ****
  • Posts: 316
Answer to Question 1

After establishing the correct total system airflow, the correct airflow through each zone is set using the zone dampers. Finally, the airflow through each individual register is adjusted using the branch duct dampers.

Answer to Question 2

To remove surface oxides and allow bonding.





 

Did you know?

Fewer than 10% of babies are born on their exact due dates, 50% are born within 1 week of the due date, and 90% are born within 2 weeks of the date.

Did you know?

Nearly 31 million adults in America have a total cholesterol level that is more than 240 mg per dL.

Did you know?

Opium has influenced much of the world's most popular literature. The following authors were all opium users, of varying degrees: Lewis Carroll, Charles, Dickens, Arthur Conan Doyle, and Oscar Wilde.

Did you know?

Critical care patients are twice as likely to receive the wrong medication. Of these errors, 20% are life-threatening, and 42% require additional life-sustaining treatments.

Did you know?

The shortest mature adult human of whom there is independent evidence was Gul Mohammed in India. In 1990, he was measured in New Delhi and stood 22.5 inches tall.

For a complete list of videos, visit our video library