Author Question: How do the Test and Balance procedures for a zoned system differ from a non-zoned system. What ... (Read 50 times)

EY67

  • Hero Member
  • *****
  • Posts: 531
How do the Test and Balance procedures for a zoned system differ from a non-zoned system.
 
  What will be an ideal response?

Question 2

Why must the copper fitting be cleaned before brazing it?
 
  What will be an ideal response?



Related Topics

Need homework help now?

Ask unlimited questions for free

Ask a Question
Marked as best answer by a Subject Expert

chloejackso

  • Sr. Member
  • ****
  • Posts: 316
Answer to Question 1

After establishing the correct total system airflow, the correct airflow through each zone is set using the zone dampers. Finally, the airflow through each individual register is adjusted using the branch duct dampers.

Answer to Question 2

To remove surface oxides and allow bonding.





 

Did you know?

The first oncogene was discovered in 1970 and was termed SRC (pronounced "SARK").

Did you know?

Today, nearly 8 out of 10 pregnant women living with HIV (about 1.1 million), receive antiretrovirals.

Did you know?

Asthma-like symptoms were first recorded about 3,500 years ago in Egypt. The first manuscript specifically written about asthma was in the year 1190, describing a condition characterized by sudden breathlessness. The treatments listed in this manuscript include chicken soup, herbs, and sexual abstinence.

Did you know?

In ancient Rome, many of the richer people in the population had lead-induced gout. The reason for this is unclear. Lead poisoning has also been linked to madness.

Did you know?

More than one-third of adult Americans are obese. Diseases that kill the largest number of people annually, such as heart disease, cancer, diabetes, stroke, and hypertension, can be attributed to diet.

For a complete list of videos, visit our video library