Author Question: How do the Test and Balance procedures for a zoned system differ from a non-zoned system. What ... (Read 101 times)

EY67

  • Hero Member
  • *****
  • Posts: 531
How do the Test and Balance procedures for a zoned system differ from a non-zoned system.
 
  What will be an ideal response?

Question 2

Why must the copper fitting be cleaned before brazing it?
 
  What will be an ideal response?



Related Topics

Need homework help now?

Ask unlimited questions for free

Ask a Question
Marked as best answer by a Subject Expert

chloejackso

  • Sr. Member
  • ****
  • Posts: 316
Answer to Question 1

After establishing the correct total system airflow, the correct airflow through each zone is set using the zone dampers. Finally, the airflow through each individual register is adjusted using the branch duct dampers.

Answer to Question 2

To remove surface oxides and allow bonding.





 

Did you know?

Interferon was scarce and expensive until 1980, when the interferon gene was inserted into bacteria using recombinant DNA technology, allowing for mass cultivation and purification from bacterial cultures.

Did you know?

The Babylonians wrote numbers in a system that used 60 as the base value rather than the number 10. They did not have a symbol for "zero."

Did you know?

You should not take more than 1,000 mg of vitamin E per day. Doses above this amount increase the risk of bleeding problems that can lead to a stroke.

Did you know?

Aspirin may benefit 11 different cancers, including those of the colon, pancreas, lungs, prostate, breasts, and leukemia.

Did you know?

Since 1988, the CDC has reported a 99% reduction in bacterial meningitis caused by Haemophilus influenzae, due to the introduction of the vaccine against it.

For a complete list of videos, visit our video library