Author Question: When installing an oil fired furnace in a confined space with a firing rate of 100,000 Btuh, what is ... (Read 67 times)

Capo

  • Hero Member
  • *****
  • Posts: 545
When installing an oil fired furnace in a confined space with a firing rate of 100,000 Btuh, what is the minimum free air opening required if the combustion air vents are directly communicating with the outside?
 
  A) 100,000 / 2,000 = 50 square inches for each grille
  B) 100,000 / 5,000 = 20 square inches for each grille
  C) 100,000 / 1,000 = 100 square inches for each grille
  D) 100,000 / 4,000 = 25 square inches for each grille

Question 2

If combustion air openings pass through horizontal ducts with 4,000 BTU input, how large should the openings measure?
 
  A) 3 inches squared B) 1 inch squared C) 4 inches squared D) 2 inches squared



Related Topics

Need homework help now?

Ask unlimited questions for free

Ask a Question
Marked as best answer by a Subject Expert

macagn

  • Sr. Member
  • ****
  • Posts: 345
Answer to Question 1

B

Answer to Question 2

A





 

Did you know?

In women, pharmacodynamic differences include increased sensitivity to (and increased effectiveness of) beta-blockers, opioids, selective serotonin reuptake inhibitors, and typical antipsychotics.

Did you know?

Everyone has one nostril that is larger than the other.

Did you know?

Elderly adults are living longer, and causes of death are shifting. At the same time, autopsy rates are at or near their lowest in history.

Did you know?

Thyroid conditions cause a higher risk of fibromyalgia and chronic fatigue syndrome.

Did you know?

In 2010, opiate painkllers, such as morphine, OxyContin®, and Vicodin®, were tied to almost 60% of drug overdose deaths.

For a complete list of videos, visit our video library