Author Question: What would be the required vacuum for an oil furnace located 5 feet above the oil tank with a ... (Read 44 times)

altibaby

  • Hero Member
  • *****
  • Posts: 562
What would be the required vacuum for an oil furnace located 5 feet above the oil tank with a horizontal run of 20 feet?
 
  What will be an ideal response?

Question 2

Why is superheating desirable?
 
  What will be an ideal response?



abro1885

  • Sr. Member
  • ****
  • Posts: 337
Answer to Question 1

5 x 1 = 5inches for vertical lift 20/10 = 2 inches for horizontal run 5+2=7 inches vacuum

Answer to Question 2

Superheating the refrigerant leaving the evaporator insures that no liquid enters the compressor. If liquid does enter the compressor it can be damaged because liquid is non-compressible.



Related Topics

Need homework help now?

Ask unlimited questions for free

Ask a Question
 

Did you know?

Disorders that may affect pharmacodynamics include genetic mutations, malnutrition, thyrotoxicosis, myasthenia gravis, Parkinson's disease, and certain forms of insulin-resistant diabetes mellitus.

Did you know?

The FDA recognizes 118 routes of administration.

Did you know?

Human neurons are so small that they require a microscope in order to be seen. However, some neurons can be up to 3 feet long, such as those that extend from the spinal cord to the toes.

Did you know?

In the United States, an estimated 50 million unnecessary antibiotics are prescribed for viral respiratory infections.

Did you know?

All adults should have their cholesterol levels checked once every 5 years. During 2009–2010, 69.4% of Americans age 20 and older reported having their cholesterol checked within the last five years.

For a complete list of videos, visit our video library