Author Question: What would be the required vacuum for an oil furnace located 5 feet above the oil tank with a ... (Read 35 times)

altibaby

  • Hero Member
  • *****
  • Posts: 562
What would be the required vacuum for an oil furnace located 5 feet above the oil tank with a horizontal run of 20 feet?
 
  What will be an ideal response?

Question 2

Why is superheating desirable?
 
  What will be an ideal response?



abro1885

  • Sr. Member
  • ****
  • Posts: 337
Answer to Question 1

5 x 1 = 5inches for vertical lift 20/10 = 2 inches for horizontal run 5+2=7 inches vacuum

Answer to Question 2

Superheating the refrigerant leaving the evaporator insures that no liquid enters the compressor. If liquid does enter the compressor it can be damaged because liquid is non-compressible.



Related Topics

Need homework help now?

Ask unlimited questions for free

Ask a Question
 

Did you know?

Street names for barbiturates include reds, red devils, yellow jackets, blue heavens, Christmas trees, and rainbows. They are commonly referred to as downers.

Did you know?

Long-term mental and physical effects from substance abuse include: paranoia, psychosis, immune deficiencies, and organ damage.

Did you know?

The average office desk has 400 times more bacteria on it than a toilet.

Did you know?

Nitroglycerin is used to alleviate various heart-related conditions, and it is also the chief component of dynamite (but mixed in a solid clay base to stabilize it).

Did you know?

Computer programs are available that crosscheck a new drug's possible trade name with all other trade names currently available. These programs detect dangerous similarities between names and alert the manufacturer of the drug.

For a complete list of videos, visit our video library