Author Question: What would be the required vacuum for an oil furnace located 5 feet above the oil tank with a ... (Read 15 times)

altibaby

  • Hero Member
  • *****
  • Posts: 562
What would be the required vacuum for an oil furnace located 5 feet above the oil tank with a horizontal run of 20 feet?
 
  What will be an ideal response?

Question 2

Why is superheating desirable?
 
  What will be an ideal response?



abro1885

  • Sr. Member
  • ****
  • Posts: 337
Answer to Question 1

5 x 1 = 5inches for vertical lift 20/10 = 2 inches for horizontal run 5+2=7 inches vacuum

Answer to Question 2

Superheating the refrigerant leaving the evaporator insures that no liquid enters the compressor. If liquid does enter the compressor it can be damaged because liquid is non-compressible.



Related Topics

Need homework help now?

Ask unlimited questions for free

Ask a Question
 

Did you know?

The familiar sounds of your heart are made by the heart's valves as they open and close.

Did you know?

The term pharmacology is derived from the Greek words pharmakon("claim, medicine, poison, or remedy") and logos ("study").

Did you know?

If you could remove all of your skin, it would weigh up to 5 pounds.

Did you know?

As many as 28% of hospitalized patients requiring mechanical ventilators to help them breathe (for more than 48 hours) will develop ventilator-associated pneumonia. Current therapy involves intravenous antibiotics, but new antibiotics that can be inhaled (and more directly treat the infection) are being developed.

Did you know?

Only one in 10 cancer deaths is caused by the primary tumor. The vast majority of cancer mortality is caused by cells breaking away from the main tumor and metastasizing to other parts of the body, such as the brain, bones, or liver.

For a complete list of videos, visit our video library