Author Question: What is the most common range for minimum velocities in a horizontal line carrying refrigerant ... (Read 28 times)

sam.t96

  • Hero Member
  • *****
  • Posts: 570
What is the most common range for minimum velocities in a horizontal line carrying refrigerant vapor?
 
  What will be an ideal response?

Question 2

In FCU's that cooling coils, how is the dehumidification condensate disposed?
 
  What will be an ideal response?



Related Topics

Need homework help now?

Ask unlimited questions for free

Ask a Question
Marked as best answer by a Subject Expert

janeli

  • Sr. Member
  • ****
  • Posts: 346
Answer to Question 1

Although the minimum velocity varies by refrigerant, pipe size, and temperature, generally accepted minimum velocities in horizontal sections of refrigerant piping are 500  750 feet per minute.

Answer to Question 2

This condensate falls into a condensate pan below the coil and is removed by gravity flow to an open sanitary drain.





 

Did you know?

People about to have surgery must tell their health care providers about all supplements they take.

Did you know?

Though the United States has largely rejected the metric system, it is used for currency, as in 100 pennies = 1 dollar. Previously, the British currency system was used, with measurements such as 12 pence to the shilling, and 20 shillings to the pound.

Did you know?

As many as 20% of Americans have been infected by the fungus known as Histoplasmosis. While most people are asymptomatic or only have slight symptoms, infection can progress to a rapid and potentially fatal superinfection.

Did you know?

The most common treatment options for addiction include psychotherapy, support groups, and individual counseling.

Did you know?

The highest suicide rate in the United States is among people ages 65 years and older. Almost 15% of people in this age group commit suicide every year.

For a complete list of videos, visit our video library