Author Question: What is the most common range for minimum velocities in a horizontal line carrying refrigerant ... (Read 42 times)

sam.t96

  • Hero Member
  • *****
  • Posts: 570
What is the most common range for minimum velocities in a horizontal line carrying refrigerant vapor?
 
  What will be an ideal response?

Question 2

In FCU's that cooling coils, how is the dehumidification condensate disposed?
 
  What will be an ideal response?



Related Topics

Need homework help now?

Ask unlimited questions for free

Ask a Question
Marked as best answer by a Subject Expert

janeli

  • Sr. Member
  • ****
  • Posts: 346
Answer to Question 1

Although the minimum velocity varies by refrigerant, pipe size, and temperature, generally accepted minimum velocities in horizontal sections of refrigerant piping are 500  750 feet per minute.

Answer to Question 2

This condensate falls into a condensate pan below the coil and is removed by gravity flow to an open sanitary drain.





 

Did you know?

Throughout history, plants containing cardiac steroids have been used as heart drugs and as poisons (e.g., in arrows used in combat), emetics, and diuretics.

Did you know?

Certain chemicals, after ingestion, can be converted by the body into cyanide. Most of these chemicals have been removed from the market, but some old nail polish remover, solvents, and plastics manufacturing solutions can contain these substances.

Did you know?

Approximately 25% of all reported medication errors result from some kind of name confusion.

Did you know?

Thyroid conditions cause a higher risk of fibromyalgia and chronic fatigue syndrome.

Did you know?

Human neurons are so small that they require a microscope in order to be seen. However, some neurons can be up to 3 feet long, such as those that extend from the spinal cord to the toes.

For a complete list of videos, visit our video library