Author Question: What is the most common range for minimum velocities in a horizontal line carrying refrigerant ... (Read 82 times)

sam.t96

  • Hero Member
  • *****
  • Posts: 570
What is the most common range for minimum velocities in a horizontal line carrying refrigerant vapor?
 
  What will be an ideal response?

Question 2

In FCU's that cooling coils, how is the dehumidification condensate disposed?
 
  What will be an ideal response?



Related Topics

Need homework help now?

Ask unlimited questions for free

Ask a Question
Marked as best answer by a Subject Expert

janeli

  • Sr. Member
  • ****
  • Posts: 346
Answer to Question 1

Although the minimum velocity varies by refrigerant, pipe size, and temperature, generally accepted minimum velocities in horizontal sections of refrigerant piping are 500  750 feet per minute.

Answer to Question 2

This condensate falls into a condensate pan below the coil and is removed by gravity flow to an open sanitary drain.





 

Did you know?

Your heart beats over 36 million times a year.

Did you know?

Disorders that may affect pharmacodynamics include genetic mutations, malnutrition, thyrotoxicosis, myasthenia gravis, Parkinson's disease, and certain forms of insulin-resistant diabetes mellitus.

Did you know?

Cyanide works by making the human body unable to use oxygen.

Did you know?

Sperm cells are so tiny that 400 to 500 million (400,000,000–500,000,000) of them fit onto 1 tsp.

Did you know?

It is widely believed that giving a daily oral dose of aspirin to heart attack patients improves their chances of survival because the aspirin blocks the formation of new blood clots.

For a complete list of videos, visit our video library