Author Question: What is the most common range for minimum velocities in a horizontal line carrying refrigerant ... (Read 75 times)

sam.t96

  • Hero Member
  • *****
  • Posts: 570
What is the most common range for minimum velocities in a horizontal line carrying refrigerant vapor?
 
  What will be an ideal response?

Question 2

In FCU's that cooling coils, how is the dehumidification condensate disposed?
 
  What will be an ideal response?



Related Topics

Need homework help now?

Ask unlimited questions for free

Ask a Question
Marked as best answer by a Subject Expert

janeli

  • Sr. Member
  • ****
  • Posts: 346
Answer to Question 1

Although the minimum velocity varies by refrigerant, pipe size, and temperature, generally accepted minimum velocities in horizontal sections of refrigerant piping are 500  750 feet per minute.

Answer to Question 2

This condensate falls into a condensate pan below the coil and is removed by gravity flow to an open sanitary drain.





 

Did you know?

Colchicine is a highly poisonous alkaloid originally extracted from a type of saffron plant that is used mainly to treat gout.

Did you know?

More than 150,000 Americans killed by cardiovascular disease are younger than the age of 65 years.

Did you know?

There are 60,000 miles of blood vessels in every adult human.

Did you know?

Patients who have undergone chemotherapy for the treatment of cancer often complain of a lack of mental focus; memory loss; and a general diminution in abilities such as multitasking, attention span, and general mental agility.

Did you know?

The shortest mature adult human of whom there is independent evidence was Gul Mohammed in India. In 1990, he was measured in New Delhi and stood 22.5 inches tall.

For a complete list of videos, visit our video library