Author Question: What would be the required vacuum for an oil furnace located 5 feet above the oil tank with a ... (Read 16 times)

altibaby

  • Hero Member
  • *****
  • Posts: 562
What would be the required vacuum for an oil furnace located 5 feet above the oil tank with a horizontal run of 20 feet?
 
  What will be an ideal response?

Question 2

Why is superheating desirable?
 
  What will be an ideal response?



abro1885

  • Sr. Member
  • ****
  • Posts: 337
Answer to Question 1

5 x 1 = 5inches for vertical lift 20/10 = 2 inches for horizontal run 5+2=7 inches vacuum

Answer to Question 2

Superheating the refrigerant leaving the evaporator insures that no liquid enters the compressor. If liquid does enter the compressor it can be damaged because liquid is non-compressible.



Related Topics

Need homework help now?

Ask unlimited questions for free

Ask a Question
 

Did you know?

Many supplement containers do not even contain what their labels say. There are many documented reports of products containing much less, or more, that what is listed on their labels. They may also contain undisclosed prescription drugs and even contaminants.

Did you know?

Colchicine is a highly poisonous alkaloid originally extracted from a type of saffron plant that is used mainly to treat gout.

Did you know?

According to the American College of Allergy, Asthma & Immunology, more than 50 million Americans have some kind of food allergy. Food allergies affect between 4 and 6% of children, and 4% of adults, according to the CDC. The most common food allergies include shellfish, peanuts, walnuts, fish, eggs, milk, and soy.

Did you know?

According to the FDA, adverse drug events harmed or killed approximately 1,200,000 people in the United States in the year 2015.

Did you know?

It is important to read food labels and choose foods with low cholesterol and saturated trans fat. You should limit saturated fat to no higher than 6% of daily calories.

For a complete list of videos, visit our video library