Author Question: The compressor in an existing split system air conditioning system is being replaced. The actual ... (Read 60 times)

brutforce

  • Hero Member
  • *****
  • Posts: 540
The compressor in an existing split system air conditioning system is being replaced. The actual line length is 35 feet. The factory charge for the condensing unit is 100 ounces. The installation instructions state that the factory charge assumes a line length of 15 feet and gives the per foot adjustment as 0.6 ounces per foot. How much refrigerant should be added to the system after the system has been evacuated?
 
  What will be an ideal response?

Question 2

Who is the most reliable source of information regarding the charge for any particular piece of equipment?
 
  What will be an ideal response?



Harbringer

  • Sr. Member
  • ****
  • Posts: 329
Answer to Question 1

Since the entire charge was removed, the factory charge plus the line adjustment should be added. The line adjustment is calculated by:

Answer to Question 2

The equipment manufacturer



Related Topics

Need homework help now?

Ask unlimited questions for free

Ask a Question

brutforce

  • Hero Member
  • *****
  • Posts: 540
Both answers were spot on, thank you once again




 

Did you know?

Fewer than 10% of babies are born on their exact due dates, 50% are born within 1 week of the due date, and 90% are born within 2 weeks of the date.

Did you know?

The immune system needs 9.5 hours of sleep in total darkness to recharge completely.

Did you know?

The B-complex vitamins and vitamin C are not stored in the body and must be replaced each day.

Did you know?

Malaria was not eliminated in the United States until 1951. The term eliminated means that no new cases arise in a country for 3 years.

Did you know?

Fungal nail infections account for up to 30% of all skin infections. They affect 5% of the general population—mostly people over the age of 70.

For a complete list of videos, visit our video library